Re: Sizing a neutral (grounded)
Originally posted by paul:
Here's a problem for you. Figure that your 9 circuits are 20 amps a piece and you're running XHHW. You've also got to run a ground wire per owners specs. What size of grounded, grounding, and ungrounded conductors do you pull and what size of GRC are you going to run?
OK I'll bite, my answers are code minimums and based on three phase being available.
Here is what I come up with using one neutral for all 9 circuits.
9 - Ungrounded conductors - 10 AWG CU XHHW
1 - Grounded conductor - 2 AWG CU XHHW
1 - Grounding conductor - 10 AWG CU XHHW
RMC - 1.25"
We end up with 10 current carrying conductors resulting in a 50% reduction in ampacity.
Also the one neutral could have a maximum current of 60 amps (3 - 20 amp circuits of the same phase) so we end up needing a 2 AWG CU neutral.
(By the way if three phase was not available the single neutral would end up being a 3/0!)
_________________________________________________
Now lets think more conventionally.
Using two-wire circuits here is what I come up with.
9 - Ungrounded conductors - 10 AWG CU XHHW
9 - Grounded conductors - 10 AWG CU XHHW
1 - Grounding conductor - 10 AWG CU XHHW
RMC - 1.25"
Using two wire circuits we have 18 current carrying conductors which per Table 310.15(B)(2)(a) get a 50% downward adjustment from Table 310.16s rating.
Because of that 50% reduction we had to increase the size of the circuit conductors so now 250.122(B) kicks in and we must increase the size of the grounding conductor as well.
So in this instance we have a total conductor count of 19 - 10 AWG XHHW, requiring a 1.25" RMC.
_________________________________________________
Now lets see what happens if I use 3 phase multiwire branch circuits.
9 - Ungrounded conductors - 12 AWG CU XHHW
3 - Grounded conductors - 12 AWG CU XHHW
1 - Grounding conductor - 12 AWG CU XHHW
RMC - 1"
By using three phase multiwire branch circuits I only had 9 current carrying conductors to deal with and a total of 13 - 12 AWG XHHW conductors to fit in the raceway.
IMO, this is a great example of how much labor and material is saved by using multiwire branch circuits.
A reduction in conductor size from 10 AWG to 12 AWG.
A reduction in raceway size from 1.25" RMC to 1" RMC.
The reduction in raceway size from 1.25" RMC to 1" is significant as you can hand bend 1" RMC but will need a power bender to bend 1.25" RMC.
If it is my choice I will stick with conventional multiwire branch circuits.
[ September 04, 2005, 07:47 AM: Message edited by: iwire ]