- Massachusetts
Re: Sizing a neutral (grounded)
Here is a example of it right from the 2002 NEC Handbook.
A 120/240-volt, single-phase, 3-wire system (branch circuits rated at 20 amperes; maximum unbalanced current of 80 amperes).
That aside I can not think of any applications of this that would save me labor and materials.
In the example above they show a 4 AWG neutral now I need to use something other than wire nuts to terminate the neutral. What ever that is will cost more and take longer to install.
Also pulling one large conductor with many small ones may result in damage to the smaller conductors.
If the installer is careful I believe it can be done safely and within the rules of the NEC.Originally posted by fleetfeet:
My point is that when and if we see this practice, is it entirely wrong (ie. hazardous, code violation, inefficient, etc.). Or, for the sake of theory, is is "workable".