Sizing a neutral

Status
Not open for further replies.

James123

Member
Location
Austin Texas
Occupation
Electrician
This is for exam prep. I know how to calculate neutral load. In exam when do you size neutral based on calculated load and when do you use 250.102 (c) (1).
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree with Don. The table provides you with the minimum size that will be large enough to carry the fault current and open an OCPD. If the calculated load requires a neutral larger then the table minimum than that's the minimum size required.
 

James123

Member
Location
Austin Texas
Occupation
Electrician
Thanks it helped a lot. I passed the master calculations portion so I don’t have to take that again. I did fail the nec knowledge portion. Ran out of time and had to guess on the last 15 questions. Any tips on finding things faster in the book.
 