TacoEngineer
Member
- Location
- Houston
- Occupation
- Electrical Engineer
Trying to gain a better understanding of sizing Electrical Cable for Motors vs Continuous Loads.
Placing correction factors & Voltage Drop sizing aside, am i correct in saying we size a cable for 125% of a Motor Nameplate FLA and 100% of a continuous load FLA?
I wanted to make sure I am sizing cables correctly, and am currently looking at a 120VAC Continuous Load of 13.33Amps.
Per spec #12 is minimum so this may be a mute point but need to make sure i have the logic down. Would i size the cable to 13.33FLA or 1.25 * 13.33FLA?
Placing correction factors & Voltage Drop sizing aside, am i correct in saying we size a cable for 125% of a Motor Nameplate FLA and 100% of a continuous load FLA?
I wanted to make sure I am sizing cables correctly, and am currently looking at a 120VAC Continuous Load of 13.33Amps.
Per spec #12 is minimum so this may be a mute point but need to make sure i have the logic down. Would i size the cable to 13.33FLA or 1.25 * 13.33FLA?