Sizing Cable: Motor FLA vs Continuous FLA

TacoEngineer

Member
Location
Houston
Occupation
Electrical Engineer
Trying to gain a better understanding of sizing Electrical Cable for Motors vs Continuous Loads.

Placing correction factors & Voltage Drop sizing aside, am i correct in saying we size a cable for 125% of a Motor Nameplate FLA and 100% of a continuous load FLA?

I wanted to make sure I am sizing cables correctly, and am currently looking at a 120VAC Continuous Load of 13.33Amps.
Per spec #12 is minimum so this may be a mute point but need to make sure i have the logic down. Would i size the cable to 13.33FLA or 1.25 * 13.33FLA?
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
For a continuous load, the conductor would need to be sized not less than 125% of load before the application of any adjustment or correction factors.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
430.24 Several Motors or a Motor(s) and Other Load(s). Conductors supplying several motors, or a motor(s) and other load(s), shall have an ampacity not less than the sum of each of the following
(1) 125 percent of the full-load current rating of the highest rated motor, as determined by 430.6(A)
(2) Sum of the full-load current ratings of all the other motors in the group, as determined by 430.6(A)
(3) 100 percent of the noncontinuous non-motor load (4) 125 percent of the continuous non-motor load.
 

TacoEngineer

Member
Location
Houston
Occupation
Electrical Engineer
Based on the responses above, it appears to be the conductor must be rated for no less than 125% of the FLA regardless of Motor or Continuous load. Does that sound correct?
 