Machiavelli999
Member
We are replacing one AC unit with another.
The existing unit is fed by a 3#6 & #10G on a 60A OCP
The new unit has a listed FLA: 46A / MCA: 52A / MOCP: 70A
Question is can I keep the cables and OCP the same for the replacement unit?
I was going to keep the cables the same since #6AWG has a 55A ampacity which is above the MCA but change the OCP to 70A. However, changing the OCP would require me to upsize the grounding conductor to #8AWG. So now I am wondering if I can keep the existing feeder as is unaltered.
The existing unit is fed by a 3#6 & #10G on a 60A OCP
The new unit has a listed FLA: 46A / MCA: 52A / MOCP: 70A
Question is can I keep the cables and OCP the same for the replacement unit?
I was going to keep the cables the same since #6AWG has a 55A ampacity which is above the MCA but change the OCP to 70A. However, changing the OCP would require me to upsize the grounding conductor to #8AWG. So now I am wondering if I can keep the existing feeder as is unaltered.