Hello,
I have a 480Vac/3Ph contactor with 120Vac coil. The specifications for the coil are 1100VA (9.16A) closing power and 12VA (0.1A) Holding Power. I believe I'd size my breaker for the holding current and choose the correct trip curve to ride out the quick closing current of the Coil. Example: a 2A miniature CB with a "C" trip curve (x5-10) so the breaker should trip if the closing power hits 10A. I'd love some advice/ recommendations.
I have a 480Vac/3Ph contactor with 120Vac coil. The specifications for the coil are 1100VA (9.16A) closing power and 12VA (0.1A) Holding Power. I believe I'd size my breaker for the holding current and choose the correct trip curve to ride out the quick closing current of the Coil. Example: a 2A miniature CB with a "C" trip curve (x5-10) so the breaker should trip if the closing power hits 10A. I'd love some advice/ recommendations.