I recently did an arc flash study on one of our job sites, it was a standard 1500 kva transformer that had a normal 400A breaker coming off its buss. I was stunned when the results came back at 70 cal/cm^2. Looking at this TCC you can see that with a such a small arcing current that it took this breaker almost 50 seconds to trip.The red curve was the current settings. The blue fuse was added to protect the panel.
With so many breakers and sizes all with different tripping curves is there an easier way than going though them one by one? Here i had little over 2.5 kA arcing current. Such a low current didn't trip the breaker and thus caused the huge arc flash.
I am trying to select breakers from a catalog but i have to test each one's time curve to make sure it wont cause a high arc flash. Is there a better way?
Any Ideas?
With so many breakers and sizes all with different tripping curves is there an easier way than going though them one by one? Here i had little over 2.5 kA arcing current. Such a low current didn't trip the breaker and thus caused the huge arc flash.
I am trying to select breakers from a catalog but i have to test each one's time curve to make sure it wont cause a high arc flash. Is there a better way?