So what would you use for the overcurrent protective device? 125% or like Texie stated
Thank you that is extremely helpful. It will be for a specific piece of equipment that will be turned on and off quite often but it is a very short supply run and there are no other Upstream Transformers. Now if I can only find a 200-amp breaker to bolt in the 400 amp panel I feel confident then will be sufficient
The next standard size provision does not apply to the primary.Lemme try:
Primary current = 45,000/(1.732X208) = 124.9A. 250% of that is = 2.5 X 124.9 = 312.3, therefore, use a 350A breaker!
Secondary current = 45,000/(1.732X 480)= 54.1A. 125% of that is = 67.6A, therefore, use a 70A breaker!
The next standard size provision does not apply to the primary.
Did you mean 22kaic? If so, the answer is no.Yes 150 is the largest for that bolt in panel, but it is 22kva....will that help at all with the in rush current on start up
The AIC rating of a breaker or panel has nothing to do with how much fault current there actually is.Yes 150 is the largest for that bolt in panel, but it is 22kva....will that help at all with the in rush current on start up
if you did that you could pretty much use anyone's enclosed CB. Might be nice to have a MCCB with an adjustable IT setting to feed the transformer.A few thoughts regarding getting a 200A OCPD for that panelboard: Have you talked to you sq D gear guy about options? I am not that familiar with SQ D panelboards, but it would think a 400A PB could take a 200A frame device. You might need some different parts or "fingers" than is currently installed (and enough real estate). Another probably simpler option is add some feed thru lugs and go to a safety switch usinga tap rule.