Should you use the nameplate or size it according to generator OCP ?
Looking at 445.13 exception I believe it is saying nameplate... right
445.13 Ampacity of Conductors. The ampacity of the conductors from the generator terminals to the first distri- bution device(s) containing overcurrent protection shall not be less than 115 percent of the nameplate current rating of the generator. It shall be permitted to size the neutral con- ductors in accordance with 220.61. Conductors that must carry ground-fault currents shall not be smaller than re- quired by 250.30(A). Neutral conductors of dc generators that must carry ground-fault currents shall not be smaller than the minimum required size of the largest conductor.
Exception: Where the design and operation of the genera- tor prevent overloading, the ampacity of the conductors shall not be less than 100 percent of the nameplate current rating of the generator.
If the generator has built in OCD (breaker) then 445.13 is a moot code and doesn't apply. You would size to the OCP.