I'm looking for some help interpreting 430.122. On a branch circuit with multiple VFDs, do I size the branch and feeder conductors based on the sum of each individual VFD input current rating multiplied by 125%? For example, if I'm using qty. (3) 3HP AB drives each with an input current rating of 7.5A, must the conductor size be capable of handling (3)*(1.25*7.5A)? I understand the OPCD sizing will remain a function of the motor FLA, but conductor size gets large very quickly if I am understanding 430.122 correctly.
Check out 430.131 which refers you to 430.53
430.131 Several Motors or Loads on One Branch Circuit
Including Power Conversion Equipment. For installations
meeting all the requirements of 430.53 that include one or more
power converters, the branch-circuit short-circuit and groundfault
protective fuses or inverse time circuit breakers shall be
of a type and rating or setting permitted for use with the power
conversion equipment using the full-load current rating of the
connected motor load in accordance with 430.53. For the purposes
of 430.53 and 430.131, power conversion equipment shall
be considered to be a motor controller.