evanc44
New member
- Location
- Columbus, NE, USA
I'm looking for some help interpreting 430.122. On a branch circuit with multiple VFDs, do I size the branch and feeder conductors based on the sum of each individual VFD input current rating multiplied by 125%? For example, if I'm using qty. (3) 3HP AB drives each with an input current rating of 7.5A, must the conductor size be capable of handling (3)*(1.25*7.5A)? I understand the OPCD sizing will remain a function of the motor FLA, but conductor size gets large very quickly if I am understanding 430.122 correctly.