When sizing conductors for primary and secondary do you have to increase the size by 125% when there is nothing but the transformer involved? The secondary side of the transformer has branch circuits that go to lights, fans, and defrost circuits in refridgerated cases?
The transformer sizes are 75KVA,45KVA,30KVA,15KVA,& 9KVA. If you take the KVA and divide by the voltage x square root of 3 you would have amps. Then size the wire correct?
The transformer sizes are 75KVA,45KVA,30KVA,15KVA,& 9KVA. If you take the KVA and divide by the voltage x square root of 3 you would have amps. Then size the wire correct?