slc410
Electrician
- Location
- Madison wi
- Occupation
- Electrician
Is the 1.25 multiplier ever used in sizing wires? I always thought that multiplier was used only for sizing overloads or circuit breakers with continuous loads.
Yes. If your sizing the wire like say for a motor load do you have to factor in the 1.25? Or wire size for any load for that matter?Are you asking does the conductor ever need to be sized at 125% of the ampere rating of the OCPD?