I have heard two diffrent versions of how to calculate for the correct sizing of conductors. Some say to calculate for the load, others say to calculate for the OCPD. The NEC under article 240.4 stipulates that you need to protect conductors against overcurrent, therefore the sizing of the OCPD is relevnet to the ampacity of the conductor that it is protecting and not the load. i will give you an expample. Let's say that you have an exsiting misc. continuous load of 286 ampers and the OCPD is rated 400 amperes. The conductors that feed this circuit are 600MCM. According to the NEC article 240.4 the OCPD is sized to protect the conductors since the 600MCM is rated at 475 at 90c. Even at 75c the conductors are rated at 420. The distance to the load is approx. 320 feet. There is really only a small voltage drop at this point. Am I correct in saying that the ampacty of the conductor must meet the the sizing of OCPD even after any derating or correction factors are done? Of course the conducots will need to be sized a minimum of 125% of the load. Why do some people stipulate that you must size to the load instead of the OCPD?