I'll buy that!
I'll buy that!
After further review........I think I'll side with you on this.
so....... note 1 in 450.3(B) is applicable in respect to possibly exceeding 125% max OCPD......but the conductors do have to be full size......
I'll buy that!
IMO you can roll that up to a 300 amp Secondary OCPD as long as the secondary conductors are sized for that.
After further review........I think I'll side with you on this.
New language in 2005 (NECPLUS comment as reference)
240.21(C): Revised to clarify that transformer secondary conductors must have an ampacity not less than the rating of the overcurrent protective device in which they terminate and that the use of the ``next higher standard rating'' is not permitted.
so....... note 1 in 450.3(B) is applicable in respect to possibly exceeding 125% max OCPD......but the conductors do have to be full size......