I am trying to figure out how to size conductors for a CNC machine. I have done a lot of research and I keep coming back to theses questions.
Does a CNC fall under Article 670 of the NEC (industrial machinery)
The size of the supply conductor shall be such as to have an ampacity not less than 125 percent of the full-load current rating of all resistance heating loads plus 125 percent of the full-load current rating of the highest rated motor plus the sum of the full-load current ratings of all other connected motors and apparatus, based on their duty cycle, that may be in operation at the same time.
If so which do I add considering there is no heaters
Is it considered a continuous load?
This is an example of one CNC Name plate I choose this one due to the largest motor being at 96amps
220/480v 3PH 60HZ
Rated capacity 30.5KVA
FLC 80.1/36.7
Largest motor is 96amps the name plate does not specify what voltage this is at.
interrupt Cap 25/7.5
Does a CNC fall under Article 670 of the NEC (industrial machinery)
The size of the supply conductor shall be such as to have an ampacity not less than 125 percent of the full-load current rating of all resistance heating loads plus 125 percent of the full-load current rating of the highest rated motor plus the sum of the full-load current ratings of all other connected motors and apparatus, based on their duty cycle, that may be in operation at the same time.
If so which do I add considering there is no heaters
Is it considered a continuous load?
This is an example of one CNC Name plate I choose this one due to the largest motor being at 96amps
220/480v 3PH 60HZ
Rated capacity 30.5KVA
FLC 80.1/36.7
Largest motor is 96amps the name plate does not specify what voltage this is at.
interrupt Cap 25/7.5