Hi,
I have heard discrepancies in approach to size an equipment grounding conductor that is on the secondary side of a transformer tap (prior to hitting the downstream overcurrent protection device). I have heard two differing responses:
1. Size it according to 250.30(A)(3) Ground Conductor which refers you to table Table 250.66.
2. Size it according to Table 250.122
I think it would be according to #1 above.
Thanks.