Dear Mr. Holt,
When sizing grounding conductor using Table 250.122 I have a concern regarding the case when, for voltage loss reduction reasons, the current-carrying conductor needs to be sized larger than the selected OCPD rating. In such cases, is it recommendable/customary to size the grounding conductor relative to the new (larger) current-carrying conductor size? For example the rating of my selected OCPD is 300A, the required conductor is a 250MCM and the minimum equipment ground conductor is a #4 AWG. If just for voltage loss reduction I need to increase the conductors from 250 to 400MCM should/can I increase the ground conductor as well? (I understand that table 250.122 does not relate to conductor area but for OCPD ratings and I don't think either that the notes to the table are applicable in my case).
If you consider the ground conductor could be sized larger can you please comment on criteria for the oversizing?
Thanks much
Alberto Gonzalez
Thanks much
Alberto Gonzalez