L Larry Iriarte New member Nov 16, 2010 #1 In the NEC 250.122, Table 250.122, how is the size of the grounding conductor determined/calculated based on the protection rating?
In the NEC 250.122, Table 250.122, how is the size of the grounding conductor determined/calculated based on the protection rating?
petersonra Senior Member Location Northern illinois Occupation engineer Nov 16, 2010 #2 Larry Iriarte said: In the NEC 250.122, Table 250.122, how is the size of the grounding conductor determined/calculated based on the protection rating? Click to expand... It comes right out of the table. A 15A OCPD requires a #14 copper, etc. There are some cases where it has to be made larger, but this is the smallest it can ever be for a branch circuit with that specific size of OCPD.
Larry Iriarte said: In the NEC 250.122, Table 250.122, how is the size of the grounding conductor determined/calculated based on the protection rating? Click to expand... It comes right out of the table. A 15A OCPD requires a #14 copper, etc. There are some cases where it has to be made larger, but this is the smallest it can ever be for a branch circuit with that specific size of OCPD.