Sierrasparky said:Bob
so you really think we all have been doing it wrong prior to the 2002 code?
I think many areas have misinterpreted it since at least 96 and maybe 93.
In the 1990 NEC the section was shorter and basically said, you could use the table for feeders and services in dwelling units. So under the 1990 NEC I agree it could be used for sub panel feeder sizing.
I don''t have the 93, so I don't know what it said then but in the 1996 NEC I find the words "that serve as the main power feeder to a dwelling unit"
Once we get to the 99 NEC they added more explanation.
"For application of this section, the main power feeder shall be the feeder(s) between the main disconnect and the lighting and appliance branch circuit panelboard(s)."
If anyone has the ROPs for those code years we could get to the bottom of this. As far as I know those ROPs are not online so someone would have to have them at home on paper.