gporter
Member
- Location
- NW Pennsylvania
For sizing feeder or service conductors, Article 220 gives you the rules by which to compute the total load. These rules contain no provisions for increasing loads by 25% for continuous loads (i.e. 220.15 says that electric heaters are to be computed at 100% of the connected load, not 125% even though they are likely to be continuous loads). However 215.2(A)(1) and 230.42(A) requires feeders and service conductors to be sized for the sum of non-continuous loads plus 125% of continuous loads. Does the load computed by Art. 220 take precedence over the sizing requirements of Art. 215 and 230?