If I am installing a 20 Amp branch circuit in support of a continuous load and intend on installing THHN, can I use the 90 degree ampacity from table 310-16 in my de-rating calculations even if I don't know my termination ratings (110-14C indicates I can)? I am currently taking an "Understanding the NEC" course at my local college and the instructor (the city Electrical Inspector) says I can as long as my calculated result does not exceed the 75 degree amount in the table 310-16. If I read on 110-14, I get the impression 60 degree ampacity is the figure to use.
Thank you
Thank you