sizing for a motor that is running over FLA.

Status
Not open for further replies.

ken Horn

Member
I have a situation where a motor is rated at 167 amps and we are pulling 205 amps and yet not tripping the overloads or the 200 amp fuses in the disconnect. We have had trouble with one leg heating and have retightened the lugs and still having trouble with it heating. How do I size my new circuit breaker which we are putting in in place of the fuses and the wiring since I am over full load amps of the motor?
 
ken Horn said:
I have a situation where a motor is rated at 167 amps and we are pulling 205 amps and yet not tripping the overloads or the 200 amp fuses in the disconnect. We have had trouble with one leg heating and have retightened the lugs and still having trouble with it heating. How do I size my new circuit breaker which we are putting in in place of the fuses and the wiring since I am over full load amps of the motor?

How confident are you in the meter readings?

Is it a true RMS meter?

Have you checked it against other meters?
 
ken Horn said:
I have a situation where a motor is rated at 167 amps and we are pulling 205 amps and yet not tripping the overloads or the 200 amp fuses in the disconnect. We have had trouble with one leg heating and have retightened the lugs and still having trouble with it heating. How do I size my new circuit breaker which we are putting in in place of the fuses and the wiring since I am over full load amps of the motor?

Instead of replacing the fuses and conductors, have you considered replacing the motor?
 
Ken, If it is still 'heating' one phase, then you still have a problem. Up sizing

the circuit breaker is not going to stop the heating problem. Find the problem

first would be my course of action.
 
Most motors will have a service factor of 15 %, thats about 16 amps in your case, but going into the SF cuts down motor life due to heat.
The load is what controls the amperage on the motor. Whats going on with the load? Bad bearing?
What type and class of overloads do you have?
And how are you measuring the current? has your meter been calibrated?
 