Like David said, might be worth looking into what voltage options POCO has. I highly doubt they will do a MV service for that low a demand. MAYBE they will do 480 in which case that may be worth it as you will only need one transformer at the end to step down to 120/240. Many POCOs these days won't even do that as they don't want oddball stuff out there, but worth a try.....if you have to do a step up / step down, i have quite a bit of experience and have two options I would suggest looking into (I have done both):
1. Standard 15 kv class step up / step down setup. I have done UG with CN #2 cable. For most of us UG is the way to go as setting poles and doing that type of OH work is a bit of a specialty. I know you said u got a guy who can set poles so maybe that is an option. IMO UG is much simpler nicer and cheaper and within the skill set of pretty much any electrician (except making up the elbow connectors which scares people but it's not a big deal). You can get surplus + used transformers pretty cheap, probably 7.2/12.47 or 7.62/13.2kv, try Solomon, Maddox, and T&R electric.
2. Do a 2kv step up step down with 2 kv PV
wire. Probably you will only need like #10 CU (this is what I have serving my house, 1900 feet but it's #12).. set it up as an MGN and you only need (1) 2kv conductor and the grounded conductor can be standard 600v rated. 3/4 conduit ! Of course you will need custom transformers, but that's not a big deal, try Hammond and olsun, they can make that for you. Of course you will pay more for transformers because of the special voltage you won't have any used/surplus options, but the wire and conduit is cheap as crap.