- Tennessee NEC:2017
- Semi-Retired Electrician
I have a couple of requests/questions concerning voltage drop.
Would someone check me on this please?
Need to run a 208V, 70A single phase circuit 425'. The feed will come out of a 208/120V 3 Ø panel.
According to the calculator I used I would need to use 2/0 to keep voltage drop to 3% and be able to have 70A available.
Now since I increased the ungrounded conductors, I need to increase the EGC.
According to my calculations I will need a 2/0 EGC.:weeping: Does that sound right?
circ. mils of 2/0 is 133100
circ. mils of #4 is 41740
133100/41740=3.18
3.18 x 41740 =132733
2/0 would be closest to 132733 (133100)
What size grounded (neutral) conductor would be needed?
The loads are just one machine that pulls 35A @ 208V and doesn't need a neutral. The others are 120V for a couple of receptacles and maybe some lights. So any increase in neutral would just be max 40A load @ the 425' distance.
133100/41740=3.18