I have the following system:
Transformer: 2.0/2.66MVA, 23KV-400V, Z=5.75%, 3ph, 50Hz, delta-wye (soild grounded)
Primary OCPD: Fused LBS close coupled to transformer
Secondary: 12ft - 4000Amp bus duct terminating in a LV Power circuit breaker
I need to size the primary side fuse for protecting the transformer as well as secondary side bus duct. Primary FLA = 67Amps
NEC 450.3A is little confusing to me. Not sure if it will be supervised or not...does the fuse to be sized 125% or 250% or 300% ? What should be the fuse size - 200amp or 225amp or something else?
Thanks in advance - RK