Sizing fuses for 400w ballast kits

Status
Not open for further replies.

ssandoval

Member
Location
League City,TX
For the sake of argument, lets say the load info on the core is missing; how do you calculate the FLA for a 400w/ 480v metal halide kit? What calculation would you use to size fuses? Is there any peak or "in-rush" associated with a ballast powering up?
 
400/480=.83

I am pretty sure there is capacitance to take care of the in-rush for the most part. Fuses are not required but always good practice(at the base of the pole that is):grin:.

If it were me, I'd use 2 or 3 amp cartridges.
 
Yeah, our district's specs require fuses in all pole bases. Problem is, they fused them with 2 amp fuses and most have blown. We re-fused them with 6 amp fuses and had no problems for over a month now. I can't figure out they would blow 2 amp fuses? Anybody?
 
Go on the advance ballast web site and look up a similar ballast. The cut sheet will provide a recommended fuse size for each voltage that the ballast could run at.

We use 2 amp Class CC fuses for 480 volt 400 watt HID fixtures and 5 amp CCs for 1000s at 480.
 
Fusing individual lights/poles is a huge troubleshooting timesaver. We have several hundred low bay lights we maintain in some dairy barns, it's a pain to find the one ballast that shorted out and took the whole string with it.:roll:
 
You didnt really say that is was a pole light, and if its not, and fixtures are just mounted here and there, AND, if area classification permits, I have drilled a 1/2" hole in the fixture side and mounted a Panel mount fuse holder....Little fuse, or Buss holder...pretty handy.....as already stated this will save troubleshooting and keep the rest of the string "on" after a ballast failure........OOPS with 480 the fuse holder mounting hole will be bigger than 1/2" "MY BAD"
 
Last edited:
has anyone fused light poles already installed

has anyone fused light poles already installed

have you done a job where the customer requested fusing existing parking lot
pole lights?

is this a complicated job? cost effective?

say about 40 poles in a multi bldg complex?
 
steveng said:
have you done a job where the customer requested fusing existing parking lot
pole lights?
yes. no. well, sort of. After I explained the benefits, they asked me to do it.

steveng said:
is this a complicated job?
No, not at all. There are inline fuseholders made specially for this purpose. They go in the handhole.

steveng said:
cost effective?

say about 40 poles in a multi bldg complex?
Well, compared to a drawn out service call playing "find the bad ballast" for 2 days, yeah, it probably is cost effective. Enhanced security is a selling point too. Instead of a bunch of lights going dark if one of the ballasts craps out hard, you'll just lose one fixture.
 
I've installed the in-line fuseholders to fuse down a whole bunch of VAV's that called for less than a 20 amp circuit. They are beyond simple to install.
 