Sizing GEC in parallel sets

Zyb

Member
Location
Maine
Occupation
Design Engineer
I have four sets of copper 250kcmil in two conduits, how do I size the GEC

1. each conduit has equal to 500kcmil so I use 1/0 copper per conduit
or
2. total equivalent conductor size is 1000kcmil (4 sets x 250kcmil) thus use 2/0 per conduit
 
The GEC is sized per the combined kcmil of the service entrance conductors and the number of raceways is not a consideration.
 
If it is an SSBJ as suggested ( installed in a feeder on the line side of the first means of disconnect, then refer to table 250.102 notes at the bottom. But in a nut shell go t the tables int he back. Find the area of the power conductor size. Multiply by the number or parallel. Then multiply by .125. (12 1/2%) that value is the area of the ground required in each conduit. Look in the able again and find the conductor size.
 
  • Like
Reactions: Zyb
1. each conduit has equal to 500kcmil so I use 1/0 copper per conduit
If this is actually a SSBJ then yes you can use the combined size of the ungrounded conductors in each raceway and T250.102(C)(1).
2. total equivalent conductor size is 1000kcmil (4 sets x 250kcmil) thus use 2/0 per conduit
A GEC would be sized according to the combined size of the ungrounded conductors in both raceways and T250.66.
 
If it is an SSBJ as suggested ( installed in a feeder on the line side of the first means of disconnect, then refer to table 250.102 notes at the bottom. But in a nut shell go t the tables int he back. Find the area of the power conductor size. Multiply by the number or parallel. Then multiply by .125. (12 1/2%) that value is the area of the ground required in each conduit. Look in the able again and find the conductor size.
thank you
 