Two Questions maybe three
1. 300A Panel, taking all the homeruns to a trough in the attic. Put ground bars in the trough to eliminate taking all the grounds down to the panel. What size ground do I need to take from panel to the ground bar in the trough? Do I need to bond each g-bar in the trough? (I have 4)?
2. Each conduit that goes from the panel to the trough, does each conduit need a ground in it? I heard this from another foreman, but could not find anywhere in the code requiring each conduit to carry a ground.
- I would like to run 1 ground sized properly to the g-bar in trough and terminate all homerun grounds there.
1. 300A Panel, taking all the homeruns to a trough in the attic. Put ground bars in the trough to eliminate taking all the grounds down to the panel. What size ground do I need to take from panel to the ground bar in the trough? Do I need to bond each g-bar in the trough? (I have 4)?
2. Each conduit that goes from the panel to the trough, does each conduit need a ground in it? I heard this from another foreman, but could not find anywhere in the code requiring each conduit to carry a ground.
- I would like to run 1 ground sized properly to the g-bar in trough and terminate all homerun grounds there.