Sizing Gutters?

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
straight line in and out ? 32"long, not wide,, wide enough for your conduits, blocks and the tap per post #2/ #7
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Hmmm. No disrespect Raider1, but I'd like to hear what others think on this.

Its all good.

Gutters are made to have multiple conduit entries in the top, bottom, etc.

Yes they are, and if they contain #4 conductors and larger the conduit entrys must meet the requirements of 376.23(B).

Chris
 

aftershock

Senior Member
Location
Memphis, TN
iwire said:
Don't forget to order a cover with that block, the NEC prohibits live exposed parts in wireways


Article please. I need to look into that for the job I am working on. If my boss argues the point I can have something to reference.
 