Let me ask this one separately.
I have a 200a, main-breaker, 3-ph hi-leg service, where the only 3-ph load is the existing roof-top AC unit somewhere around 30a. I plan to size A and C phases, as well as the neutral, as usual for the load.
The question is how to size the hi-leg service entrance and feeder conductors. Since the over-current protection will be the 200 main breaker, how small can the hi-leg conductor be and still be protected?
To go with a fusible main for the purpose of mixing sizes can get expensive, as can finding a 200/30/200 main breaker. I can't be the first one to come up with this situation, can I? As always, all input welcome.