I'm connecting a 400KW load bank to a 650KW generator, 480V. That calculates to about 481 amps per phase fully loaded. The steps in the load bank are fused at : 2 @ 80 amps, 3 @150 amps. That's 610 amps. It seems that the load bank is fused higher than it's rated kw. Does anyone know if there's a reason for this, or if my calculations are wrong, or if something else is amiss? How shall I size the conductors?