A feeder tap protected by 125A Circuit Breaker in a subpanel connects to a 480:208/120 Transformer. I understand that the feeder tap provisions of 240.21(B)(3) concerning the sizing of the primary transformer conductors apply if the total length of the primary and secondary conductors is no greater than 25 ft. However, if the length does exceed 25 ft. is it correct to apply 210.20 for the sizing of both the primary conductor and the OCPD in the subpanel using the load connected to the transformer as a criterion (assuming, of course, that none of the other conditions such as manufacturing buildings, etc. come into play)?
Many thanks for your comments.
Heinz R.