Hi. Continuing on my project to create an electrical plan for our Makerspace.
I have calculated the loads for the subpanels, 5 at 240v 3ph, 6 at 208/120, and 1 at 480v 3ph.
The building has a 500KVA 208/120 utility transformer, that feeds a meter bank in the building with a 1600A main breaker.
A number of meter sockets are available, including 2 at 400a and several at 200a. (208Y120)
The previous design build company seemed to think that was plenty to serve our loads. I planned to use the first 400a 208/120 for general purpose receptacles, LED lighting, and HVAC loads.
Much of the equipment is designed for 240v rather than 208, so I planned to use the second 400a circuit to feed an autotransformer to provide 240 3ph, to serve both single and 3ph loads. Lastly, I only have one machine that needs 480v (waterjet cutter), but planned to run air compressor and dust collection blower on 480 also due to length of circuits.
I have created a spreadsheet that calculate the panel schedules. It adds up the VA on each phase, totals them up, derates the general purpose receptacles over 10kva, adds 125% of largest motor load and lighting load (as calculated at 2VA per foot, not actual loads)
Panel schedule link (dropbox)
if I add up the 5 240v panels, I get a total of 282077 VA or 679A at 240v.
the 480v panel is 101224va or 122a at 480v
the 6 208/120 panels add up to 311398 va or 864a at 208v.
If i divide the volt amps above by 208, I get the amps at the 208 supply voltage: 240>208 783a. 480>208 281a. 208=208 864a.
These figures add up to more than the main breaker for the building (1600a at 208)
If anyone has a chance to glance over the spreadsheets and make sure they seem correct, that would be great.
Is the derating for the general purpose outlets correct for the 2014 NEC? 100% to 10KVA, then 50% of remainder? (light industrial usage)
The big question: having calculated all the subpanels, how do I calculate the main power panels for each voltage?
Do I treat them like a subpanel, and add up all the loads on all the subpanels, derate the GP receptacles, and add 125% for cont. loads and largest motor?
Do you add the subpanel VA or Amps together to get the proper figure?
Or, is there some way to allow for load diversity, or derate a portion of the loads to fit the two 400a and one 200a feeds available?
All my equipment loads are on individual branch circuits.
I have two 240v 50a 1ph welder plugs without dedicated equipment. How do I calculate for these? Full load? 0?
Unlike a manufacturer, it is very unlikely that all the equipment will ever be used at the same time, or even half of it. Usage will be quite variable.
It is a new buildout, I don't have any historical information on power usage.
I know this is a lot of information, I've got a good week or so of work into this. A little direction to bring this to conclusion would be MOST appreciated!
If I've got to bite the bullet and put in a new 480v service, I'd rather know now....
Thank you,
Bryan
I have calculated the loads for the subpanels, 5 at 240v 3ph, 6 at 208/120, and 1 at 480v 3ph.
The building has a 500KVA 208/120 utility transformer, that feeds a meter bank in the building with a 1600A main breaker.
A number of meter sockets are available, including 2 at 400a and several at 200a. (208Y120)
The previous design build company seemed to think that was plenty to serve our loads. I planned to use the first 400a 208/120 for general purpose receptacles, LED lighting, and HVAC loads.
Much of the equipment is designed for 240v rather than 208, so I planned to use the second 400a circuit to feed an autotransformer to provide 240 3ph, to serve both single and 3ph loads. Lastly, I only have one machine that needs 480v (waterjet cutter), but planned to run air compressor and dust collection blower on 480 also due to length of circuits.
I have created a spreadsheet that calculate the panel schedules. It adds up the VA on each phase, totals them up, derates the general purpose receptacles over 10kva, adds 125% of largest motor load and lighting load (as calculated at 2VA per foot, not actual loads)
Panel schedule link (dropbox)
if I add up the 5 240v panels, I get a total of 282077 VA or 679A at 240v.
the 480v panel is 101224va or 122a at 480v
the 6 208/120 panels add up to 311398 va or 864a at 208v.
If i divide the volt amps above by 208, I get the amps at the 208 supply voltage: 240>208 783a. 480>208 281a. 208=208 864a.
These figures add up to more than the main breaker for the building (1600a at 208)
If anyone has a chance to glance over the spreadsheets and make sure they seem correct, that would be great.
Is the derating for the general purpose outlets correct for the 2014 NEC? 100% to 10KVA, then 50% of remainder? (light industrial usage)
The big question: having calculated all the subpanels, how do I calculate the main power panels for each voltage?
Do I treat them like a subpanel, and add up all the loads on all the subpanels, derate the GP receptacles, and add 125% for cont. loads and largest motor?
Do you add the subpanel VA or Amps together to get the proper figure?
Or, is there some way to allow for load diversity, or derate a portion of the loads to fit the two 400a and one 200a feeds available?
All my equipment loads are on individual branch circuits.
I have two 240v 50a 1ph welder plugs without dedicated equipment. How do I calculate for these? Full load? 0?
Unlike a manufacturer, it is very unlikely that all the equipment will ever be used at the same time, or even half of it. Usage will be quite variable.
It is a new buildout, I don't have any historical information on power usage.
I know this is a lot of information, I've got a good week or so of work into this. A little direction to bring this to conclusion would be MOST appreciated!
If I've got to bite the bullet and put in a new 480v service, I'd rather know now....
Thank you,
Bryan