sizing motor conductors

Status
Not open for further replies.

KFLinkII

Member
When Sizing motor conductors does 240.4D apply? As in 14 wire is good for 15 amps 12 wire is good for 20 amps and 10 wire is good fo 30 amps. 240.4G says part III, IV, V VI, VII apply but does not mention part II Motor conductors.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No, 240.4(D) does not apply to motor branch circuits. You are free to use the values listed in 310.16 without the restrictions of 240.4(D).
 

KFLinkII

Member
Can you give me a code reference? Because the way I read 240.4G It does not apply to motor conductors part II of 430
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Part II of Article 430 does not contain any overcurrent protection rules, it just tells you how to size the conductors. The overcurrent protection rules are found in parts III, IV, V, and VI as referenced in 240.4(G).