mario8449
- United States
I am confused when it comes to sizing feeder cables going out to a motor from a starter. I have always done 125% of whatever is full load amps on the motor but just recently I was told that I should actually size the motor feeders based on size of the MCP. I will list an example below. The system I am considering for the example below is an AB MCC with a bucket composed of a MCP and starter.
100 A MCP (instantaneous is the only thing that can be changed)
AB Size 3 starter
30 HP Motor (say 36 FLA for this example)
36A x 1.25 = 45 A
Therefore, does my feeder going to the motor from the starter need to protect for 45 A or does it need to protect for 100 A?
Thanks for the help in advance.
AB Size 3 starter
36A x 1.25 = 45 A