Here's my question. I have a street lighting system. The lights are equipped with receptacles on top and 2- 100W lights. My service is 3 ph 4 wire 120/208Y vac. The run is about 600' with lights poles distributed about every 75 to 100'. The lights have a multitap ballast and are being fed 1 phase 208 vac. The receptacles are 120 vac @ 20 amps. The lights are fed with one 15 A two pole breaker. The receptacles are fed from 3 20A single pole breakers (3 receptacles to a breaker).
Question #1: To avoid voltage drop on receptacle circuits from exceeding 3% I have oversized the conductors over the length to maintain a less than 3% drop at the furthest receptacle. My wire starts at #1/0 and is reduced in size (between the respective lights) as the length of the run becomes shorter. All 3 receptacles circuits are fed with a common neutral. Am I required to oversize the neutral because of the larger potential load (in addition to the oversizing required to accomodate the voltage drop)? Furthermore am I required to derate the oversized conductors to 80% to account for the bundling (2 ungrounded lighting conductors and four ungrounded receptacle conductors) in addition to the voltage drop upsizing already performed?
Question #2:
Are GFCI receptacles required to have a separate neutral wire (one per receptacle) per the code? to work correctly?
Are GFCI Breakers required to have a separate neutral wire (one per breaker)per the code? to work correctly?
Question #3:
For multiwire branch circuits is there any NEC Code requirements that specify a minimum of 1 neutral for every three multiwire branch circuit conductors?
Your thoughts are appreciated.
Question #1: To avoid voltage drop on receptacle circuits from exceeding 3% I have oversized the conductors over the length to maintain a less than 3% drop at the furthest receptacle. My wire starts at #1/0 and is reduced in size (between the respective lights) as the length of the run becomes shorter. All 3 receptacles circuits are fed with a common neutral. Am I required to oversize the neutral because of the larger potential load (in addition to the oversizing required to accomodate the voltage drop)? Furthermore am I required to derate the oversized conductors to 80% to account for the bundling (2 ungrounded lighting conductors and four ungrounded receptacle conductors) in addition to the voltage drop upsizing already performed?
Question #2:
Are GFCI receptacles required to have a separate neutral wire (one per receptacle) per the code? to work correctly?
Are GFCI Breakers required to have a separate neutral wire (one per breaker)per the code? to work correctly?
Question #3:
For multiwire branch circuits is there any NEC Code requirements that specify a minimum of 1 neutral for every three multiwire branch circuit conductors?
Your thoughts are appreciated.