sizing NM-B and SE-R

Status
Not open for further replies.

royta

Senior Member
*Edited to remove the question. I've got the book right in front of me. I'm not sure why I needed a confirmation on something so simple as this. :)

[ September 07, 2004, 05:21 PM: Message edited by: royta ]
 
Re: sizing NM-B and SE-R

Editited to remove the question :confused: What was the question??
 
Re: sizing NM-B and SE-R

Oh, it was about what size of SE or NM-B cable to use on a 50A circuit. From what I've read, NB cable is to be sized at 60C, and SE can be sized at 75C. So #6 for NM, and #6 for SE (Al).

Sometimes, even though I found the answer I'm looking for by myself, I still want reassurance from others that I'm on the money. Know what I mean?
 