Does anyone have the history or backstory if any? On why NM-B is still beholden to the 60degC column even when landing both ends on 75degC equipment. I mean we haven't used NM in forever. NM-B came out in what 1985?!
Is it just an oversight that 334.80 doesn't provide the same exception that 110.14(C)(1)(b) allows for other wire types. Are the panels just not talking or is there a specific reason they don't want NM-B using the 75degC rating on rated equipment? Is this worth a public comment before the window closes in 2 weeks?
ref 110.14(C)(1)(b) conductors with higher than 75°C ratings provided the conductor ampacity does not exceed the 75°C ampacity of the conductor size used. This condition also permits the conductors to be used at ampacities higher than 75°C if the equipment is listed and identified for the higher rating.
Is it just an oversight that 334.80 doesn't provide the same exception that 110.14(C)(1)(b) allows for other wire types. Are the panels just not talking or is there a specific reason they don't want NM-B using the 75degC rating on rated equipment? Is this worth a public comment before the window closes in 2 weeks?
ref 110.14(C)(1)(b) conductors with higher than 75°C ratings provided the conductor ampacity does not exceed the 75°C ampacity of the conductor size used. This condition also permits the conductors to be used at ampacities higher than 75°C if the equipment is listed and identified for the higher rating.