Does 240.4 (max ocpd on a 14awg is 15) apply to the sizing of motor conductors. If not is it specifically stated or is it just "understood as"
Hopefully moderators are paid...if not they need to add a tip button...a lot of thinking alone pushes you into a downward spiral of what ifs and how abouts...your clarify and guidance is superb (tip button here) thank you so muchThe clue is in the wording
240.4
..........................................unless otherwise permitted or required in 240.4(A) through (G).
(G) Overcurrent Protection for Specific Conductor Applica tions. Overcurrent protection for the specific conductors shall be permitted to be provided as referenced in Table 240.4(G).