It is an exclusive electrical system for the fire-fighting pump.
The 13.8kV transmission line is an aerial type and is exclusive to the customer.
The transformer will be installed next to the fire fighting pump house.
There will be no other electrical system in this area than the exclusive fire fighting system.
We are in Brazil, but our client requires compliance with NFPA 20.
We are preparing the electrical project and the complete specification of the electrical panel that will perform the activation of the fire-fighting pump.
I have no doubt about the current value of the circuit breaker and its functions.
Our question is in the specific point of NFPA 20 about the circuit breaker, that is, should the FRAME of the circuit breaker support the blocked rotor current or only the circuit breaker current sensor?
Example:
Circuit breaker (Compact NSX100 model with only MA Unit Trip - Schneider): Has Frame In 100A and Magnetic Unit Pickup (Im) = 9 to 14 * In
The 13.8kV transmission line is an aerial type and is exclusive to the customer.
The transformer will be installed next to the fire fighting pump house.
There will be no other electrical system in this area than the exclusive fire fighting system.
We are in Brazil, but our client requires compliance with NFPA 20.
We are preparing the electrical project and the complete specification of the electrical panel that will perform the activation of the fire-fighting pump.
I have no doubt about the current value of the circuit breaker and its functions.
Our question is in the specific point of NFPA 20 about the circuit breaker, that is, should the FRAME of the circuit breaker support the blocked rotor current or only the circuit breaker current sensor?
Example:
Circuit breaker (Compact NSX100 model with only MA Unit Trip - Schneider): Has Frame In 100A and Magnetic Unit Pickup (Im) = 9 to 14 * In