What size fuses need to be installed in a service disconnect that feeds 2 240V 100A rated main lug only panels? I think they would be 100A fuses but others are telling me 200A.
What size fuses need to be installed in a service disconnect that feeds 2 240V 100A rated main lug only panels? I think they would be 100A fuses but others are telling me 200A.
I think you would need more info to determine what size fuses are appropriate.What size fuses need to be installed in a service disconnect that feeds 2 240V 100A rated main lug only panels? I think they would be 100A fuses but others are telling me 200A.
What size fuses need to be installed in a service disconnect that feeds 2 240V 100A rated main lug only panels? I think they would be 100A fuses but others are telling me 200A.
Why? I just did a 400 amp service split into two 225amp mlo panels. I ran 500 into a wireway, than tapped down to 3/0 per 240.21(b)1. All went well at inspection.you have to protect each MLO panel with 100A OCPD (or smaller). Depending on the load calculations this could be a single 100A (or smaller) OCPD, or muitiple OCPD, but neither panel can be protected by an OCPD rated greater than 100A.
Why? I just did a 400 amp service split into two 225amp mlo panels. I ran 500 into a wireway, than tapped down to 3/0 per 240.21(b)1. All went well at inspection.
Sent from my SM-G950U using Tapatalk
Why? I just did a 400 amp service split into two 225amp mlo panels. I ran 500 into a wireway, than tapped down to 3/0 per 240.21(b)1. All went well at inspection.
Why? I just did a 400 amp service split into two 225amp mlo panels. I ran 500 into a wireway, than tapped down to 3/0 per 240.21(b)1. All went well at inspection.
Are you not familiar with tap rules?225 amp panels can handle a maximum of 225 amps. If you are protecting them with a 400 amp breaker, it will not trip before they burn up. The fact that it passed inspection only means the inspector did not catch the violation.
Are you not familiar with tap rules?
Sent from my SM-G950U using Tapatalk
408.36 Overcurrent Protection. In addition to the re-
quirement of 408.30, a panelboard shall be protected by an
overcurrent protective device having a rating not greater
than that of the panelboard. This overcurrent protective de-
vice shall be located within or at any point on the supply
side of the panelboard.
Why is it a violation? 240.21(B)(1), 1b states - "not less than the rating of the EQUIPMENT containing an overcurrent device(s) supplied by the tap conductors..."MLO equals violation, not sure why you passed inspection.
Ocpd required for the panel board is the 400 amp disconnect next to it.Forget the tap rules for a second, where's the OCPD required for the panelboard?
Ocpd required for the panel board is the 400 amp disconnect next to it.
Look, I can't keep arguing this. I see your point in regards to 408.36 and respect your opinion.How does the 400 amp OCPD protect the 225 amp panels according to 408.36?
Look, I can't keep arguing this. I see your point in regards to 408.36 and respect your opinion.
But fact is i was taught how to build this service a decade ago, and have used it many times. Never had a problem. But i wouldn't brag about the inspectors around here either.
I didnt mean to hijack this thread from OP. I have no hesitations on joining a different thread
Ok. Tap rule states RATING of EQUIPMENT containing an over current device(S). My panel is the equipment that is rated, and i have overcurrent devices. My 400 amp is a single point of disconnect, so no more than 6 disconnects.IMO it's fine to keep it in this thread as your installation is germane to the OP. The fact is that your installation contains two violations, one being the OCPD required to protect the panel is not the correct size (225 amps) and also the need for an OCPD at the end of the tap conductors.
As i said, i understand your concern in regards to 408, and i respect your opinion. You give good advice on this forum. But for this one, you can tell me im wrong till your blue in the face. Ill keep doing it till they take the (S) out of the 10ft tap rule
That's fine with me you can install it anyway that you like