jtester said:Frequently the neutral isn't bonded to the CT can. In that case, our POCO requires a #6 ground to a driven rod, or to the grounding electrode system if nearby.
It doesn't make sense to base it on the service main breaker size since it is upstream of that. In fact, there probably is no OCPD in the circuit upstream of the CT cabinet to operate. You're just dealing with touch potentials.
Bea said:Trevor is correct and the bonding jumper sized based on 250.66
chocho77 said:Is anybody on the same page?
iwire said:I have never seen a meter or CT can that I had to install a jumper in, all arive to me factory bonded, the neutral connections are bolted directly to the steel enclosure.
Thank you,Don!don_resqcapt19 said:Chocho,
Even with nonmetallic conduit there is no reason to install this jumper...it would be a violation of 310.4. All of the grounding of the electrical equipment on the line side of the service disconnect as well as the disconnect itself is done by a connection to the grounded conductor.
Don
russ said:They must make CT cans both ways, because I've never seen one with the grounded conductor bonded to the pan.
We only use metal conduit (RMC or IMC) so it's not a problem.
In this case (Non Metalic Raceway) I don't see any reason not to use 250.122.
250.102 Equipment Bonding Jumpers.
(C) Size ? Equipment Bonding Jumper on Supply Side of Service. The bonding jumper shall not be smaller than the sizes shown in Table 250.66 for grounding electrode conductors. Where the service-entrance phase conductors are larger than 1100 kcmil copper or 1750 kcmil aluminum, the bonding jumper shall have an area not less than 12? percent of the area of the largest phase conductor except that, where the phase conductors and the bonding jumper are of different materials (copper or aluminum), the minimum size of the bonding jumper shall be based on the assumed use of phase conductors of the same material as the bonding jumper and with an ampacity equivalent to that of the installed phase conductors. Where the service-entrance conductors are paralleled in two or more raceways or cables, the equipment bonding jumper, where routed with the raceways or cables, shall be run in parallel. The size of the bonding jumper for each raceway or cable shall be based on the size of the service-entrance conductors in each raceway or cable.
The bonding jumper for a grounding electrode conductor raceway or cable armor as covered in 250.64(E) shall be the same size or larger than the required enclosed grounding electrode conductor.
That's my case-the neutral is "floating" in the CT cabinet(NOT bonded)russ said:They must make CT cans both ways, because I've never seen one with the grounded conductor bonded to the pan.
We only use metal conduit (RMC or IMC) so it's not a problem.
In this case (Non Metalic Raceway) I don't see any reason not to use 250.122.
Why not bond it in both places...the code permits the grounded conductor to be used for all required bonding on the line side of the service disconnect.Another option is to bond the neutral to the CT can and Ufer ground
and leave it "floating" in MDP.
chocho77 said:For both options I still need Equipment Bonding Jumpers sized per table 250.66.
Yes,I agree with you,Don!This was the easiest fix after the wire and rodsdon_resqcapt19 said:Chocho,
Why not bond it in both places...the code permits the grounded conductor to be used for all required bonding on the line side of the service disconnect.
Don