sizing of grounding conductor
sizing of grounding conductor
CHOCHO77
What type of system are we talking about? I'm assuming it is that which is described in 250.24(c). I agree with those who basically said that you wouldn't have a grounding conductor on the line side of the service disconnect. Most service equipment I've seen has the neutral bonded to the case, or the means to bond it. Installing a grounding conductor of the wire type would create parrallel paths for neutral current. And yes you are required to bond one side of a conductive raceway, so the easiest way would be PVC.
hope this was some help
ibew441dc
sizing of grounding conductor
CHOCHO77
What type of system are we talking about? I'm assuming it is that which is described in 250.24(c). I agree with those who basically said that you wouldn't have a grounding conductor on the line side of the service disconnect. Most service equipment I've seen has the neutral bonded to the case, or the means to bond it. Installing a grounding conductor of the wire type would create parrallel paths for neutral current. And yes you are required to bond one side of a conductive raceway, so the easiest way would be PVC.