I've got an optional standby panel with something like 16 -80 freezers on it (they happen to be 208V-sinlge phase and approximately 2kVA each). I generally, in keeping with Article 440.22, take these at 100% of their nameplate rating. I have a couple of questions.
1) Am I correct that there is no allowance in the code for applying a diversity factor. Realistically, the compressors cycle on and off and I know that when you put a meter on such panelboards, the actual demand load is consistently below 40% of the connected load.
2) If the code provides no relief here, as a practical matter, I'd be interested in the groups experience with regard to the actual demand load seen from such a panel.
Much appreciated,
Mike