sizing overcurrent devices for residential services

Status
Not open for further replies.

remo

Member
When a calculated demand load for a multi-family building is applied,does the NEC state that the Main has to be at a 125% on TOP of the calculated demand load?
 

bennie

Esteemed Member
Re: sizing overcurrent devices for residential services

When you get to sizing the service, you will find it is less than the total of all individual calculated loads.
 

bob

Senior Member
Location
Alabama
Re: sizing overcurrent devices for residential services

When you use Article 220 to caculate the load,
the 1.25 factor is not required.
 