When a calculated demand load for a multi-family building is applied,does the NEC state that the Main has to be at a 125% on TOP of the calculated demand load?
 
Re: sizing overcurrent devices for residential services

When you get to sizing the service, you will find it is less than the total of all individual calculated loads.
 
Re: sizing overcurrent devices for residential services

When you use Article 220 to caculate the load,
the 1.25 factor is not required.
 