We have an inspector demanding we put the following A/C on a 60 amp breaker and fuses, Nameplate reads:
Minimum Circuit Ampacity = 35 amps
Minimum overcurrent = 45 amps
Maximum overcurrent = 60 amps
Inspector (probably not an electrician) is citing 440.12 (pretty much whole article) and we fail to see where this applies to his argument. We believe that 440.22 applies..... using 175% we come up with a little over 48 amps and we are on a 50 amp breaker and 50 amp fused disconnect. Before you respond with just do it ..... homeowner has a federal pacific panel and so far has refused to let us upgrade it (at his cost, of course). We replaced furnace and a/c... my feeling is once we replace the breaker in the panel, we basically own the panel should problems arise. Any thoughts? or can anyone back up the inspectors argument? or any ideas on the ideas on liability if we replace a breaker in an FPE --- as a rule we don't work on FPE equipment other than replacement.
Minimum Circuit Ampacity = 35 amps
Minimum overcurrent = 45 amps
Maximum overcurrent = 60 amps
Inspector (probably not an electrician) is citing 440.12 (pretty much whole article) and we fail to see where this applies to his argument. We believe that 440.22 applies..... using 175% we come up with a little over 48 amps and we are on a 50 amp breaker and 50 amp fused disconnect. Before you respond with just do it ..... homeowner has a federal pacific panel and so far has refused to let us upgrade it (at his cost, of course). We replaced furnace and a/c... my feeling is once we replace the breaker in the panel, we basically own the panel should problems arise. Any thoughts? or can anyone back up the inspectors argument? or any ideas on the ideas on liability if we replace a breaker in an FPE --- as a rule we don't work on FPE equipment other than replacement.