I have a motor control panel that contains controls, contactors and thermal overloads for 3 different motors as fas as I understand by the wiring diagram only one motor can run at a time. This control panel does not contain a disconnect switch nore any sort of overcurrent protection (fuses, breaker, ect)
all three motors are 460V 3 phase
one is a 10hp, one is a 7.5hp, the last is a 1.5hp
I am trying to figure out how to select a proper size overcurrent protection breaker to put on the feeder to the control panel . the manufacturer engineer has told us to add up all the loads and just simply get a breaker that will handle the load. But this can not be correct if only one motor can run at a time. As i would think that adding all of the load up would create an overcurrent that would possibly never trip because only one motor can run at a time. Am I understanding this incorrectly ?
all three motors are 460V 3 phase
one is a 10hp, one is a 7.5hp, the last is a 1.5hp
I am trying to figure out how to select a proper size overcurrent protection breaker to put on the feeder to the control panel . the manufacturer engineer has told us to add up all the loads and just simply get a breaker that will handle the load. But this can not be correct if only one motor can run at a time. As i would think that adding all of the load up would create an overcurrent that would possibly never trip because only one motor can run at a time. Am I understanding this incorrectly ?